[PATCH] hwmon: (scpi) Add slope and offset to SCP sensor readings
Carlo Caione
carlo at endlessm.com
Wed Mar 1 08:16:36 PST 2017
On Wed, Mar 1, 2017 at 4:01 PM, Guenter Roeck <linux at roeck-us.net> wrote:
> On 03/01/2017 05:20 AM, Carlo Caione wrote:
>>
>> From: Carlo Caione <carlo at endlessm.com>
>>
>> The temperature provided by the SCP sensors not always is expressed in
>> millicelsius, whereas this is required by the thermal framework. This is
>> for example the case for the Amlogic devices, where the SCP sensor
>> readings are expressed in degree (and not milli degree) Celsius.
>>
> Are you saying that SCPI does not specify or provide the units to be used
> when reading values, and thus effectively just reports a more or less
> random number ?
AFAICT the standard does not specify the units to be used for the
values or a way to get that information. For the Amlogic case the SCP
returns the value of the temperature in degree celsius and I'm not
sure how common is that.
[cut]
>> - *temp = value;
>> + slope = thermal_zone_get_slope(zone->z);
>> + offset = thermal_zone_get_offset(zone->z);
>
>
> This is conceptually wrong. The functions return -ENODEV if thermal is
> disabled.
> While a negative slope does not make sense, a negative offset does.
Yeah, but in that case we would have already failed to register the
thermal zone at all in devm_thermal_zone_of_sensor_register().
> The code in the thermal subsystem does not clarify well how slope and offset
> are supposed to be used. Since coming from the thermal subsystem, one would
> think
> that the thermal subsystem would apply any corrections if they are supposed
> to be software correction values, but that does not appear to be the case,
> leaving it up to drivers to use or not use the provided values.
Yes, this is my understanding also considering this comment here:
http://lxr.free-electrons.com/source/drivers/thermal/of-thermal.c#L1006
So apparently the slope and offset values are left to be used by the
driver, that's why I was changing the temperature driver to use those
values.
> This is kind of odd; the values are thermal subsystem attributes/properties,
> and one would think that they are to be used there unless they are supposed
> to be
> written into hardware. Given that, I'd rather wait for the API to be
> clarified
> instead of jumping into using it.
Zhang, Eduardo (+CC)
can you clarify a bit this point?
> There are secondary problems with this approach; other drivers such as lm90
> which
> support the thermal subsystem have their own means to specify and use the
> offset
> (since it needs to be programmed into the chip registers).
I fail to see how this is related to my patch. If no coefficient is
defined in the thermal zone node in the DT the framework sets slope=1
and offset=0, so in the hwmon driver nothing changes.
> Also, this would only solve the problem for temperatures and does not
> address
> the generic problem (ie voltage and current values).
This problem is specific for the interaction between the hwmon SCPI
driver and the thermal subsystem. Look for example at the board I'm
working with one single thermal zone using the temperature data coming
from SCP:
scpi_sensors: sensors {
compatible = "arm,scpi-sensors";
#thermal-sensor-cells = <1>;
};
thermal-zones {
soc_thermal {
thermal-sensors = <&scpi_sensors 0>;
coefficients = <1000 0>;
trips {
control: trip-point at 1 {
temperature = <80000>;
hysteresis = <1000>;
type = "passive";
};
};
cooling-maps {
cpufreq_cooling_map {
trip = <&control>;
cooling-device = <&cpus THERMAL_NO_LIMIT THERMAL_NO_LIMIT>;
};
};
};
};
trip points are defined in milli degree Celsius while the temperature
returned by the scpi_sensors node is in degree Celsius. Without using
the coefficients property and my changes how can I make the cooling
map working fine?
Thanks,
--
Carlo Caione | +39.340.80.30.096 | Endless
More information about the linux-amlogic