[PATCH 2/3] thermal: Add Mediatek thermal controller support
Punit Agrawal
punit.agrawal at arm.com
Wed Sep 30 04:07:04 PDT 2015
Sascha Hauer <s.hauer at pengutronix.de> writes:
> Hi Punit,
>
> On Wed, Sep 30, 2015 at 10:36:14AM +0100, Punit Agrawal wrote:
>> Hi Sascha,
>>
>> Re-posting a comment from v7. Perhaps you missed it...
>
> Uh, sorry. In fact I didn't miss it and I thought I have answered it.
> Appearantly I haven't.
>
>> > + struct mtk_thermal *mt = bank->mt;
>> > + int temp, i, max;
>> > + u32 raw;
>> > +
>> > + temp = max = INT_MIN;
>> > +
>> > + for (i = 0; i < bank_data[bank->id].num_sensors; i++) {
>> > + raw = readl(mt->thermal_base + sensing_points[i].msr);
>> > +
>> > + temp = raw_to_mcelsius(mt, raw);
>> > +
>> > + /*
>> > + * The first read of a sensor often contains very high bogus
>> > + * temperature value. Filter these out so that the system does
>> > + * not immediately shut down.
>> > + */
>> > + if (temp > 200000)
>> > + temp = 0;
>> > +
>>
>> If the bogus value is only the first time the sensor is read, instead of
>> filtering here, you could call mtk_thermal_bank_temperature at probe
>> time when you are initialising the banks and ignore the returned value.
>
> It seems that after initialization the hardware needs some time to
> settle before correct values can be read. Doing what you suggest would
> mean we have to delay the boot by several 100ms. I'd rather not do that.
Fair enough. Thanks for clarifying.
>
> Sascha