[PATCH 04/13] thermal: Fix not emulating critical temperatures

Sascha Hauer s.hauer at pengutronix.de
Thu Mar 26 11:55:37 PDT 2015


+Cc Amit who implemented the emulation code.

On Thu, Mar 26, 2015 at 02:13:47PM -0400, Carlos Hernandez wrote:
> On 03/26/2015 11:53 AM, Sascha Hauer wrote:
> >- The code should only accept an emulated temperature when the emulated
> >   temperature is lower than the critical temperature. Instead the code
> 
> Why?
> Emulating temperatures higher than critical temperature is useful
> for testing. For instance it allows one to validate that critical
> action (i.e. shutdown) is triggered.

Not emulating critical temperatures was the intention of the original
patch adding the emulation code, but it was implemented wrongly. I just
fix to the intended behaviour.
However, I also find emulating critical temperatures useful. I could
also remove the check instead of fixing it if we can agree on that
behaviour.

Sascha

-- 